Welcome to Our Community

Some features disabled for guests. Register Today.

Lead 1010 and Ferrite cores

Discussion in 'CNC Mills/Routers' started by jda70az, Mar 16, 2021.

  1. jda70az

    jda70az Well-Known
    Builder

    Joined:
    Nov 11, 2020
    Messages:
    122
    Likes Received:
    16
    Hi.
    Just got a bunch of different sizes and was wondering
    Are there any cords on the Lead 1010 machine that shouldn't have
    Ferrite cores? Just wanna make sure.

    I have clamped them on
    OB Interface cord.
    XYZ Probe cord
    all 4 Motor cords and 3 Limit switch cords.
    Also on the power supply cord that connects to Black Box.
    And Meanwell power cord
     
  2. Peter Van Der Walt

    Peter Van Der Walt OpenBuilds Team
    Staff Member Moderator Builder Resident Builder

    Joined:
    Mar 1, 2017
    Messages:
    14,927
    Likes Received:
    4,291
    No you can add them to everything. EMi is a mystical beast. We have seen cases where the cnc wiring wasnt the culprit, a spare usb cable hanging out the back of the PC was (nothing connected, it just about acted like an antenna), and even mouse, keyboard cables. so dont rule out other cables either around the PC (if emi was giving you USB problems)
     
  3. jda70az

    jda70az Well-Known
    Builder

    Joined:
    Nov 11, 2020
    Messages:
    122
    Likes Received:
    16
    ok cool thx
     
    Peter Van Der Walt likes this.
  4. Peter Van Der Walt

    Peter Van Der Walt OpenBuilds Team
    Staff Member Moderator Builder Resident Builder

    Joined:
    Mar 1, 2017
    Messages:
    14,927
    Likes Received:
    4,291
    Also, Ferrites helps, but can't do magic. Best to also look at the source of the EMI. Spindle not earthed? Vacuum hose without an earth? Fixing the cause is better than trying to shield everything around it
     
  5. RobFromLDMS

    Builder

    Joined:
    Oct 16, 2018
    Messages:
    8
    Likes Received:
    3
    And watch out for the dreaded ground loop. Single point grounding only, ground only one end (the source end) of all screened cables, one connection to ground from each device. ALL ground connections MUST be star connected to a single grounding point. That alone will clear up 95% of your noise problems. The other 1% is voodoo magic.
     
  6. Giarc

    Giarc OpenBuilds Team
    Staff Member Moderator Builder Resident Builder

    Joined:
    Jan 24, 2015
    Messages:
    3,008
    Likes Received:
    1,676
    What is the other 4%? ;) Or are those the ferrites?:)

     
    #6 Giarc, Mar 31, 2021
    Last edited: Mar 31, 2021

Share This Page

  1. This site uses cookies to help personalise content, tailor your experience and to keep you logged in if you register.
    By continuing to use this site, you are consenting to our use of cookies.
    Dismiss Notice